[a / b / c / d / e / f / g / gif / h / hr / k / m / o / p / r / s / t / u / v / vg / vm / vmg / vr / vrpg / vst / w / wg] [i / ic] [r9k / s4s / vip / qa] [cm / hm / lgbt / y] [3 / aco / adv / an / bant / biz / cgl / ck / co / diy / fa / fit / gd / hc / his / int / jp / lit / mlp / mu / n / news / out / po / pol / pw / qst / sci / soc / sp / tg / toy / trv / tv / vp / vt / wsg / wsr / x / xs] [Settings] [Search] [Mobile] [Home]
Board
Settings Mobile Home
/diy/ - Do It Yourself


Thread archived.
You cannot reply anymore.


[Advertise on 4chan]


The air coming out of the registers is room temperature. I listened to the condenser outside and it's not making any humming noises, fan is spinning just fine. Could it still be a bad capacitor? Maybe tomorrow when it's light out I could try cleaning the condenser coils. If it's not the coils or capacitor does that mean it's low on refrigerant? The unit is 6yrs old. Tried to do research before posting (lennox system in typical ranch house)
>>
>Check air filter
>Check if condensor coils are hogged
>Check if compressor is running
>Check if little pipe is hot and large pipe is cold
>>
>>2788271
thanks I gotta work on this tomorrow so will keep posted
>>
Try rubbing money on the outside bits.
>>
>>2788271
In addition to this, also check the condensate pump if you have one. Depending how it's wired, it could keep the cooling bits from kicking on if it's full.
>>
It’s either your pan switch, compressor contactor or the start components for the compressor. Go outside and mash the contactor in with a sharpie or stick, not metal. If the compressor comes on you’re not getting power contactor coil or the contactor is bad. If the compressor still doesn’t come on get a multi meter and check the capacitance of the compressor capacitor. If that’s good take the plug off the compressor and check between all 3 pins 2 at a time and see if you have resistance. Then check each pin to the case of the compressor and see if you have ohms to ground. Open terminals between each other is bad. Ohms to ground is bad
>>
>>2788266
I was about to tell you the same thing >>2788379
anon did.
If it's a new unit it might also have an error code display on the main PCB you can look up.
>>
File: IMG_4704.jpg (2.96 MB, 3024x4032)
2.96 MB
2.96 MB JPG
>>2788276
OP here. I'm pretty sure it's the capacitor. When I touched the capacitor with a screwdriver, I didn't get any spark. I can't see any reading with my multimeter, but it's just a standard multimeter. Ordered one for $13 bc my local hardware want's $32 and the box stores don't carry them.

Also I cleaned out my coils. Reminder for anyone viewing this thread to clean your AC coils as summer begins.
>>
>>2788514
you're not supposed to get a spark.
you read a capacitor with microfarads.
do you have 240 across the contactor? is the compressor pulling amperage?
>>
>>2788540
Videos were showing a spark lol, they were saying its a short but I got a new capacitor and I'm still in the same boat.

I'm going to call someone tomorrow, because I can make it through the night
>>
>>2788276
This >>2788374

Check your condensation drain system, if you don’t know what that is and haven’t ever cleaned it, then 90% chance that is the issue.

Yours probably won’t look as retarded as picrel, but look for that little white PVC cap with 2 wires coming out of it. Lift the top of thing up. There’s a little float in there. If it’s not draining, the float rises and shuts off the compressor. Yours may not be inline like the pic, but rather a little PVC “L” coming out of the side of the air handler.

Easiest way is if you have a wet/dry vac, go outside and find the outlet and such the shit out. Pour some vinegar down the drain by where the float thing is once every month or two to keep it clean.
>>
>>2788568
>Check your condensation drain system
Thanks for the input, when it clogs up it shuts off the fan outside. In my case the fan is running. I went down and poured a bottle of water in the pump to verify though and it is in fact running with no problems.
>>
>>2788559
Push in the contactor and see if the compressor starts. If the compressor doesn't start and you have power to the contactor then check your thermostat.

>>2788540
You can read a capacitor with an ohm meter, its just not super accurate. By discharging the capacitor with a screw driver (Or a 20k ohm resistor) you are dissipating any charge left in the cap. If the capacitor has no power in it there might be something wrong with the wires leading into the capacitor.

>>2788266
Post schematic inside of the condensing unit and post any other schematics for your unit. Compressors shouldn't be shitting out so soon.
>>
File: IMG_4708.jpg (2.45 MB, 3024x4032)
2.45 MB
2.45 MB JPG
>>2788578
Might can find more. Pushed in the contactor and both the fan and compressor start and stay on. Compressor sounds fine, fan runs fine.

Has it just leaked refrigerant at this point?
>>
>>2788580
if:
>your air filter, evap coil, condenser coils are clean
>you have no air blockage
>compressor, condenser fan, blower fan are all running
>you have little to no temp split across your evap coil
>you have no frost or ice forming on the evap coil or inlet of the condenser
you got a leak
>>
>>2788599
Air filter clean, just cleaned condenser coils they were this >>2788514
No air blockage
Compressor, condenser fan, blower fan are all running - Check

Only thing I haven't checked are the evap coils in the crawl. I'm going to set up for someone to come tomorrow, but maybe I'll take a peak at those in the morning
>>
>>2788602
Did it go from 100% working fine to no AC at all immediately? Or did it seem like it was struggling to keep up for a little bit? Last time I had a leak, I noticed at least half a day of it working real hard to keep the house below 80F before it was all gone. But that was a slower leak.

Fuck those EPA licenses btw. Us hard working rednecks should be able to refill that leaky mess ourselves.
>>
>>2788606
This was the first time I've turned it on since last summer. It was struggling to keep up but I'm in NC and we see some pretty high temps in summer.
>Fuck those EPA licenses btw
YES that's literally why I have to call someone
>>
>>2788580
So because you have the compressor able to run, you probably haven’t had a burnout or lacked refrigerant to run. Pull your thermostat and do a continuity test on the terminals on the back. You can also check the secondary 24 volt side of the transformer and see if that’s working.

This doesn’t sound like a leak, this sounds like you have an issue somewhere between the transformer and the thermostat. A call for cool isn’t turning on the compressor. What does the control board look like? Do you see any burned traces or resistors?
>>
>>2788611
When the thermostat calls for cool, the compressor runs as well

>What does the control board look like? Do you see any burned traces or resistors?
No
>>
>>2788606
>Fuck those EPA licenses btw
Thing has 0 refrigerant and they want $600 just for the refrigerant
>>
I replaced my caps and contactor assembly in my unit for 40 bucks and bought a new fan and blade set for 250 dollars for my 25 year old unit before i sold my house. it was just the contactors but i just started replacing shit to make it work.
>>
>>2788952
>has 0 refrigerant
You need to locate and fix the leak.

>>2788952
>they want $600 just for the refrigerant
Depending on the refrigerant, that may not be as outrageous as it seems.
>>
>>2788963
yeah I checked prices of refrigerant and you're right. he's doing a leak test now. might as well have him do the whole job at this point.
>>
>>2788966
FUCK it's leaking out of the evap coils and the condensor. he's saying they'll have to replace both these. is this correct?
>>
>>2788974
>leaking out of the evap coils and the condensor.
leak in evap is common.
leak in the evaporator and condenser at the same time is sus
>>
>>2788606
>Us hard working rednecks should be able to refill that leaky mess ourselves.
You can always employ don't ask, don't tell doctrine. It is up for sale with you checking the little
>>2788952
$600 just for the refrigerant
That'd be the price if you were buying a small quantity, so he's still fucking you over.
My 5 ton runs on about 8-9lbs of r-410a, worth maybe $50. If you have an R-22, that's more expensive, but not $600.
>>2788974
>it's leaking out of the evap coils and the condensor
Important thing to remember is that HVACfagging can be done by IQ 85 retards, so you might be talking to a retard taught to fire the parts canon. Shoot some UV dye in and see where it leaks out, might be EZ fix.
>>
>>2788610
>>Fuck those EPA licenses btw
>YES that's literally why I have to call someone
Not really, you could've figured out all of this yourself without besmirching your goody two-shoes status.
>You can check pressure on your unit and find out all of the refrigerant was returned to mother earth Gaia just like EPA intended
>You can also do whatever work you want on empty copper pipes
IF you think elf on the shelf is watching you and will report you to get your good goy points revoked, you just need to call a certfag to fill it once you're done pressure testing.
>>
>>2788974
did he show you the leak?
>>
>>2788974
jb weld the leak
>>
OP is retarded, I don’t understand how people really have unanswerable questions in this day and age with the internet and YouTube. If OP is still listening or anyone in the same boat with a pair of balls wants advice, I’m this scenario you should buy guages ($150) and a tank of refrigerant off eBay if it’s not R22. Adding gas is easy as fuck. Then put in some leakstop. Leakstop used to be garbage that killed your compressor or clogged your expansion valve immediately but whatever the new shit is works fine. You could also do it right and replace the evaporator coil but this is a big job even for someone in the field. You’ll get fucked by whoever you call to the extreme of of 4-5k, they want you to buy a new unit instead of fixing it. If your system is R22 you’re dumb and missed the boat by a few decades, just replace that shit. I work in the field and 90% of calls are just peopl being cheapskates and limping units along or neglecting maintenance and prematurely killing their equipment. Take it upon yourself to research how this shit works, it’s very simple
>>
>>2789007
im glad a2ls are gonna scare the shit out of homeowners so they never take this awful advice. you expect people to do subcooling? fix their leaks? these "people" cant even change an air filter once every 6 months.
>>
>>2789003
I think he took pictures
>>
hey AC experts how difficult would it be to get a 50 gallon drum of ammonia and make a machine to chill my house to zero degrees?
>>
>>2789007
where do you live? i'll pay you 2k maybe 3k to come do that
>>
File: Screenshot-3.jpg (73 KB, 827x964)
73 KB
73 KB JPG
>>2789018
I'm retired from repair and maintenance - I still get called to change lightbulbs...