alright dudes help me out here cause I'm driving myself bananas over this>sets of outlets tied to 2 different breakers were working as of last fall - as of this spring none worked>breakers were not tripped and did not trip when pushing the test buttons on the outlets or the breaker itself>figured I needed replacement breakers (as seen in image, the #2 and #3 from the top)>same fucking issue, when I press the test buttons on outlets/breaker it does not trip the breaker>however at least this time the outlets shine their red light so power is at least getting to themI've reset all outlets that have buttons, taken apart and inspected each outlet and does not appear to be wiring problems. I don't even know where the fuck to go from here, appreciate any advice!
>>2993202The test function of the outlet should not trip the breaker. It should only turn the outlet itself off. The test button on the breaker not turning off the breaker is an issue though. Do you have a multimeter? Have you confirmed that proper voltage is reaching the outlets?
It reads about 40% power for power coming from the middle 2 breakers. Top/bottom ones have 100
>>2993202>willingly using afci (always fucking causing issues) breakers Its probably some neutral nonsense since those things will not work if you're sharing a nuteral with any other circut.